I have a situation where a 200 amp main breaker panel is installed in an outbuilding which then feeds a 100 amp panel in the residence (this was done to upgrade to 200 amp service when the outbuilding was built). The auxiliary panel in the residence still has the 100 amp main breaker, but the ground and neutral were isolated. This was done 8 years ago and there have been no problems observed until now.
Here is what happened: The 200 amp main breaker and the 100 amp breaker in the outbuilding went out simultaneously when the homeowner manually turned off the main breaker to add a recep to an existing circuit and then turned the breaker back on. I considered it alarming that both breakers would go bad simultaneously, but we replaced them both and then started looking for the cause of the problem. Everything seems to be fine in the outbuilding. There is constant 120 volts at the lugs in the residence where the 100 amp panel is fed. There is tight connection of these conductors as well. However, at the terminals of the main breaker in the residence, there is intermittent voltage drop - enough to cause the lights to dim/flicker. Turning on one breakers one at a time and/or testing one circuit at a time only seems to decrease the frequency of the occurrence of the voltage drop but will not make it go away. It is apparent that the problem is either internally in the main breaker of the auxiliary panel or in the connection of the main breaker to the buss. The main breaker is not bolt-on, and the 100 amp panel is packed full including several tandem breakers, so I recommended replacing the entire panel with a new 100 amp panel with more circuit capacity. This would seem sure to fix the apparent problem of the intermittent voltage drop.
But, what really concerns me and has me perplexed is why would 3 breakers go "bad" at once...and where did the problem start...and, if it started in the auxiliary panel, why would it affect the other two breakers upstream. I don't want to swap the 100 amp panels and just put a bandaid on the problem only to have it arise again later on.
Any suggestions?
Any suggestions?