Please provide an example of what you’re proposing.Are we allowed to interpolate
no. of current carrying conductors = 12Please provide an example of what you’re proposing.
You would not linearly interpolate, but you can use formula 310.15(B). For correction factors near 1.0, linear interpolation may give you the same answer as the formula, but the formula is the correct way to do it.Are we allowed to interpolate Table 310.15(B)(1) 2020 - Ambient Temp. Correction Factors
Clearly not, as the table specifies a full range of conductor sizes: 4-6, 7-9, etc. So you are stuck using the factor for whichever interval your installation falls within.& Table 310.15(C)(1) Adjustment Factors for More Than Three Current-Carrying Conductors?