Hello All. So i have a new PRL1X panel that was installed - This is a (MLO) panel. The rating for the whole panel was for FULLY 22KAIC, because the fault at that panel was 14KAIC. Taking a closer look at it, it turned out that the branch breakers that were installed were rated for 10KAIC, so they looked into it and realized that Eaton sent them the wrong breakers. Now they are going to change all the branch breakers on that panel to 22KAIC.
My understanding for eaton PRL1X per their cutsheet for MLO, The short-circuit rating of the MLO assembled panelboard will be fully rated based upon the lowest rated branch circuit devices or may be series rated with an approved upstream device. In my case all the branch circuits will be rated for 22KAIC. BUT, when i look at the panel sticker it says this: feed and subfeed panels are limited for use on a system of delivering not more than 10,000, unless...... etc (see attached picture). Does the panel also need to get changed out? or changing the branch breakers to 22KAIC turns it into fully rated for 22KAIC?
Thank you!!
My understanding for eaton PRL1X per their cutsheet for MLO, The short-circuit rating of the MLO assembled panelboard will be fully rated based upon the lowest rated branch circuit devices or may be series rated with an approved upstream device. In my case all the branch circuits will be rated for 22KAIC. BUT, when i look at the panel sticker it says this: feed and subfeed panels are limited for use on a system of delivering not more than 10,000, unless...... etc (see attached picture). Does the panel also need to get changed out? or changing the branch breakers to 22KAIC turns it into fully rated for 22KAIC?