Intrinsic Safety Requirements

Status
Not open for further replies.

czangerle

Member
We sell and rent diesel driven pumps with control panels. These panels operate off of floats that go into the water. We have two different kinds of panels - one operates of 12 Volt the other off 24 Volt. What is required in order to make our floats intrinsically safe?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Intrinsic Safety Requirements

Why do you want them to be intrinsically safe? That is normally used in Classified areas to prevent explosions.
Don
 

czangerle

Member
Re: Intrinsic Safety Requirements

One of our customers is placing these floats in a hazzardous area (according to them) and is requiring we supply them a control panel with floats that is intrinsically safe when used in this application.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Intrinsic Safety Requirements

You install a IS relay. See NEC article 504. Your control panels may need to be UL listed as IS.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Intrinsic Safety Requirements

Is the pump suitable for pumping flammable liquids? Is the pump itself in the classified area? Is the pump suitable for installation in a classified area?
Don
 