Intrinsic Safety

Status
Not open for further replies.

phsfrog

Member
We have designed a circuit to lower a 12 Volt power source to 1.25 Volts with a current limit of, I think, 30mA. The location is Class 1 Division 1 Group D is there any place I can find the information of what is considered intrically safe for this location.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
The general US domestic Standard is ANSI/UL 913, Intrinsically Safe Apparatus and Associated Apparatus for Use in Class I, II, and III, Division 1, Hazardous (Classified) Locations. Also see ANSI/ISA RP 12.06.01-2002, Wiring Methods for Hazardous (Classified) Locations Instrumentation ? Part 1: Intrinsic Safety and read Article 504 very carefully. Your design will require third party certification.
 

phsfrog

Member
A third party certification will require the NRTL to certify the circuit correct or will there have to be another company certify the circuit?
 

bobgorno

Senior Member
Location
Colorado
NRTL that is accepted by AHJ, OSHA, etc. Normally in US that would be UL or FM.

Better off finding an off the shelf solution that is pre-approved.
 