R Rai136926 Member Location seattle, wa Jun 6, 2017 #1 once the intrinsically safe circuit passes through the first seal off can it be installed per chapter 3 wiring methods?
once the intrinsically safe circuit passes through the first seal off can it be installed per chapter 3 wiring methods?
Smart $ Esteemed Member Location Ohio Jun 6, 2017 #2 Rai136926 said: once the intrinsically safe circuit passes through the first seal off can it be installed per chapter 3 wiring methods? Click to expand... You are not limited to just Chapter 3 wiring methods. You can use any wiring method that would otherwise be appropriate for a non-hazardous classified area.
Rai136926 said: once the intrinsically safe circuit passes through the first seal off can it be installed per chapter 3 wiring methods? Click to expand... You are not limited to just Chapter 3 wiring methods. You can use any wiring method that would otherwise be appropriate for a non-hazardous classified area.
rbalex Moderator Staff member Location Mission Viejo, CA Occupation Professional Electrical Engineer Jun 6, 2017 #3 In addition to Smart$'s comment, see Section 504.10(C). It's not common, but a manufacture may add a restriction or two.
In addition to Smart$'s comment, see Section 504.10(C). It's not common, but a manufacture may add a restriction or two.