Jpflex
Electrician big leagues
- Victorville
- Electrician commercial and residential
I have a 5 hp motor, 230, 460, 190 and 360 volt options, 3 phase, nameplate full load amps ranges confusingly listed at 12 & 3/6, 17, 9.55, and 4.78, service factor 1.15, continuous duty, efficiency at 88.5%, power factor 85%, design B, RPM 3520
System runs 440 volt 3 phase
Wire
NEC code chart 7.6 Full Load Current amperes x 1.25% = wire good to 9.5 amperes after derating or minimum code 14 AWG wire
Overload protection
I chose smallest full load ampere rating on motor name plate 4.78 i amperes x 1.25% = 5.97 amperes so if this is max I cannot go over this or go next size up to 6 amperes if heater on NEMA starter is not standard?
Overcurrent protection
7.6 FLC x 800% if using instantaneous breakers 60.8 I amperes max or 19 i amperes if using inverse time breakers
This pictured breaker may be too small if it were an instantaneous breaker BUT HOW DO I KNOW IF THIS WERE AN INSTANTANEILOUS OR INVERSE BREAKER?
Or if the breaker does not clearly label if it’s inverse or instantaneous how do I determine this?
Wire
Overload protection