Alwayslearningelec
- NJ
- Estimator
Is it code to have lighting circuits fed from inverter in different conduits that lights feed from normal lighting panels ?
Always a spec thing but NEC requires EM circuits to be separate from normal?I believe that the inverter output circuits are considered emergency circuits which would require separation.
So theres true emergency , legally required and optional standby?"emergency circuits" is somewhat a relative term. Art 700 addresses true "emergency" circuits but the term is often used for Art 701 Legally Required and Art 702 Optional Standby and the mixing of circuits is handled differently within those Articles. You need to determine what class of system you are working with, true "emergency" or Art 701, 702.
yepSo theres true emergency , legally required and optional standby?
The NYC code amendments removed legally required standby. Someone told me that there has been an update to this but I'm not sure if that's true.So theres true emergency , legally required and optional standby?
ARTICLE 701
Legally Required Standby Systems
ARTICLE 701
Legally Required Standby Systems. Delete the article in its entirety and add a FPN to read as follows:
FPN: All legally required standby systems are classified as emergency systems.
So the amendments did not remove optional?The NYC code amendments removed legally required standby. Someone told me that there has been an update to this but I'm not sure if that's true.
No but you're inverter is likely not providing optional standby.So the amendments did not remove optional?
I thought that was answered. It depends on the classification of the circuit (area) as to it being a true "emergency" circuit or otherwise.Anyone else have input whether inverter circuits need to be in separate conduits ?
No it's providing constant power to EM fixtures or I'm wondering if it's just back up. I don;t think so based on floor plan circuit/panel desgination.No but you're inverter is likely not providing optional standby.
Yea, guess your right. Need to determine that. Article 700 will clarify what "true" emergency is considered?I thought that was answered. It depends on the classification of the circuit (area) as to it being a true "emergency" circuit or otherwise.
To me that vague. How do I determine that ?Barring any NYC changes noted in Post#8:
Emergency Systems. Those systems legally required and classed as emergency by municipal, state, federal, or other codes, or by any governmental agency having jurisdiction
Needs to be EM egress lighting for what?There needs to be EM egress lighting it's highly likely that is what is depicted on the drawing which makes it EM
Lighting for egress. When an emergency happens you need to be able to see the way out. You definitely need separate conduitsNeeds to be EM egress lighting for what?