Inverter Circuits

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Is it code to have lighting circuits fed from inverter in different conduits that lights feed from normal lighting panels ?
 
I believe that the inverter output circuits are considered emergency circuits which would require separation.
 
"emergency circuits" is somewhat a relative term. Art 700 addresses true "emergency" circuits but the term is often used for Art 701 Legally Required and Art 702 Optional Standby and the mixing of circuits is handled differently within those Articles. You need to determine what class of system you are working with, true "emergency" or Art 701, 702.
 
"emergency circuits" is somewhat a relative term. Art 700 addresses true "emergency" circuits but the term is often used for Art 701 Legally Required and Art 702 Optional Standby and the mixing of circuits is handled differently within those Articles. You need to determine what class of system you are working with, true "emergency" or Art 701, 702.
So theres true emergency , legally required and optional standby?
 
So theres true emergency , legally required and optional standby?
The NYC code amendments removed legally required standby. Someone told me that there has been an update to this but I'm not sure if that's true.

ARTICLE 701
Legally Required Standby Systems
ARTICLE 701
Legally Required Standby Systems. Delete the article in its entirety and add a FPN to read as follows:
FPN: All legally required standby systems are classified as emergency systems.
 
No but you're inverter is likely not providing optional standby.
No it's providing constant power to EM fixtures or I'm wondering if it's just back up. I don;t think so based on floor plan circuit/panel desgination.

The inverter does have a separate cabinet with batteries but I think that in case of power loss.


1704814732524.png1704814673827.png
 
I thought that was answered. It depends on the classification of the circuit (area) as to it being a true "emergency" circuit or otherwise.
Yea, guess your right. Need to determine that. Article 700 will clarify what "true" emergency is considered?
 
Barring any NYC changes noted in Post#8:

Emergency Systems. Those systems legally required and classed as emergency by municipal, state, federal, or other codes, or by any governmental agency having jurisdiction
 
Barring any NYC changes noted in Post#8:

Emergency Systems. Those systems legally required and classed as emergency by municipal, state, federal, or other codes, or by any governmental agency having jurisdiction
To me that vague. How do I determine that ?
 
Engineer/architect should have already done so,.
The fact that the circuit is labeled "EM" would lead me to believe it was emergency but infinity is well versed in these matters,.. see what he says,
 
There needs to be EM egress lighting it's highly likely that is what is depicted on the drawing which makes it EM.
 