Hello:
We are taught by manufacturers that inverters have balanced outputs; the current on L1 is the same as that on L2. Thus, in Enphase (residential) solar systems and Tesla storage systems, for example, the software measures a single line (through CT's) and multiplies that number by two, to arrive at the actual solar production.
The question: Let's say we measure 7A on L1. Is the total production in Watts equal to 120V x 7A=840W x 2 for a total of 1.68kW or is the total production 7A x 2=14A x 240 for 3.36kW?
I suspect the answer has to do with phasing but, otherwise I'm perplexed...
Thanks.
We are taught by manufacturers that inverters have balanced outputs; the current on L1 is the same as that on L2. Thus, in Enphase (residential) solar systems and Tesla storage systems, for example, the software measures a single line (through CT's) and multiplies that number by two, to arrive at the actual solar production.