I am having trouble figuring out how to deal with 75?C terminal temperature rating requirements and 90?C cable with respect to Inverter output circuit sizing.
The inverter FLA is 1176A at 270V. 1176 * 1.25 = 1470A. A 1600A breaker is used, and the conductor must be rated for 1600A. - 240.4(C)
The temperature range for this environment is 41?-45?C.
My proposed method is the following:
I can use (5) parallel sets of 400 kcmil, Cu cable. Per the 90?C column: 380 * 0.87 * 5 = 1653A > 1600A. Checks out.
Now when it comes to terminals, the argument is that they will not see the full 1600A. The terminals will only see 1176A. The 1.25 is only used for OCPD devices not fully-rated, and doesn't make sense to use here. Per the 75?C column: 335 * 0.82 * 5 = 1373A > 1176A. This also checks out.
Is this the correct line of thought?