Inverters and 110.26
tortuga
Greetings all we frequently install SMA 'Sunny Boy' inverters.
I have always considered inverters to fall under 110.26 rules for working clearance, and it usually is not a problem to meet 110.26.
Currently we have a project where a inverter is going to be installed in a laundry room in a multi family complex and the 'best' place to put the inverter is on the wall behind a cloths washer.
Now that PV systems have a Rapid Shutdown/DC disconnect initiator and I am wondering if 110.26 applies to inverters any more? (or ever did) as you would could safely de-energize the inverter from both AC and DC before servicing it.
I guess my question is two part
A) does a 'DC disconnect initiator' qualify as a 690 Part III. Disconnecting Means:
690.13 "Photovoltaic System Disconnecting Means. Means
shall be provided to disconnect the PV system from all wiring
systems including power systems, energy storage systems, and
utilization equipment and its associated premises wiring.
(A) Location. The PV system disconnecting means shall be
installed at a readily accessible location."
and
B Are there any other provisions in 690 that require working space around an inverter?
Thanks in advance.
tortuga
Yes, it applies to the inverter, always has. Behind the washer is not going to be code compliant.
Thanks for the reply are you just going off 110.26 in general?
I was just looking at 705.70:
705.70 Interactive Inverters Mounted in Not Readily Acces-
sible Locations. Interactive inverters shall be permitted to be
mounted on roofs or other exterior areas that are not readily
accessible. These installations shall comply with (1) through (4):
(1)A dc disconnecting means shall be mounted within sight
of or in the inverter.
(2)An ac disconnecting means shall be mounted within sight
(3)An additional ac disconnecting means for the inverter shall
comply with 705.22.
(4)A plaque shall be installed in accordance with 705.10.
jaggedben
705.70 has nothing to do with working space.
With most string and central inverters it strains credulity to argue that you will never have to examine them while energized. Just about any trouble shooting will require taking voltage readings in an open disconnect section. Microinverters are an exception since there's nothing to open up.
Carultch
There's a big difference between it being in a "not readily accessible location" because you have to remove obstacles, vs because you have to get a portable ladder to get to it. Especially an appliance that is a 2-person job to move out of the way. We all see nature fill the vacuum of working space from building user habits, but it should at least start correctly without any intentional device occupying the space.
That article about inverters in "not readily accessible locations" was meant for inverters in locations, where you need a portable ladder to get to the inverter. Flat roof systems where you need a portable ladder to get through the hatch, or carport column where it is intentionally out of reach from the general public. Not inverters where an appliance is in the way.
tortuga
Thanks for both of your thoughts I admit its not an ideal situation, buts its the owners preference and its a public laundry room for a multifamily complex, not a residential laundry room.
The only other location it could go (with proper working space) would make it a likely head knocker with a low washer door bordering the side of the working space.
Or at greater expense to the owner putting it outside.
I can make the case 110.26 sub paragraph (A) does not apply, as its unlikely it would need to be accessed while energized. There are two disconnects you can stand in front of and take voltage readings.
If you got DC going in and no AC coming out, the inverter is likely getting replaced.
One would not need to reach the inverter quickly during a emergency, as its just equipment at this point since there are "Readily Accessible" disconnects to de-energize it within sight.
110.26, the first paragraph seems to require general access to equipment but not ready access:
110.26 Spaces About Electrical Equipment. Access and working space shall be provided and maintained about all electrical
equipment to permit ready and safe operation and maintenance
of such equipment.
The case that would would need to be made is that the inverter is 'accessible' as defined by the NEC if all you need to do is move a large washer out of the way.
While it makes a great deal of common sense as you both point out to put the inverter in a 110.26(A) location I am not seeing a specific NEC requirement (in the 705) for an inverter to be "Readily Accessible".
And I think that behind a washer it will get no tampering from the public.
Currious if you all have more thoughts?
Thanks
ggunn
Thanks
All I can say is that I do not believe that such an installation would pass inspection with any of the AHJs I deal with.
tortuga
Thanks ran this by the AHJ, awaiting him to contemplate it also.
I am not enough of a solar guru to point to a code section that prohibits it.
tortuga
This has little to do with solar per se.
Well the interactive inverters marketed for solar often contain AFCI's and other overcurrent devices.
What my AHJ and I have concluded is an interactive inverter does not require working space as long as its:
1) Accessible without the use of tools
or modifying building finish.
2) Not likely to require examination, adjustment,
servicing, or maintenance while energized.
3) Contains no fuses or circuit breakers including AFCI's.
tortuga
As I said above, (2) is going to be hard to come by.
Well this case is closed for me now, AHJ approved.
Some of these interactive inverters are kinda of a set it and forget it system, you could put one up in a drop ceiling like a transformer IMO. They have a ethernet port and just plug in to a buildings network. All the settings you need from a web interface.
The key word the AHJ looked at in 110.26(A) is "likely".
There was nothing in the inverter manual about regular maintenance while energized.
There would be no need for an emergency responder to access the inverter quickly.
With all the new requirements around DC rapid shutdown there is not really much NEC concern about the inverter.
Now an Outback Power off grid inverter, like I used to see thats another story, they had built in over-current devices, those are basically a mini load center.
jaggedben
I can't tell you how many times I've had to service an inverter and troubleshoot it with either AC or DC energized and the cover off. You're working with an AHJ who's ignorant about solar, is about all I have left to say. Lucky for you, I guess. Man, if our company could have the money back from every time we failed an inspection over the years because our installers didn't diligently measure the working space... :roll:
ggunn
Likewise. We'd never have gotten away with that one in any jurisdiction I know of.
tortuga
While I agree some inverters may need to be examined while energized, and as a field electrician your the one doing all of this quite often (hopefully with proper PPE!).
In my opinion for 110.26(A) to legally apply with the 2017 NEC as it stands, it would have to be likely that most inverters would need to be examined while energized, like you would a service disconnect or a battery bank.
There are many things electricians may choose to examine or test while energized, junction boxes,transformers, motors, phase converters and none of them require 110.26(A) working space.
If a piece of equipment is having a problem you can de-energize the equipment from a 110.26(A) location and do what you need to do to create a safe working space to re-energize for examination and testing.
The AHJ has seen quite allot of solar, however there is a law in Oregon that inspectors have to cite a particular section of code if they are going to fail an inspection, and the state makes code interpretations on a state wide basis. I would never try to pull one over on him, that would ruin our relationship. He knows that if I am the designer on a job I am going to push hard for what our client wants, and our client is a small solar company. :)
All this being said, I really appreciate both of your input as it gives me a sense of standard practices around the country, and Ill press for a common sense location as it was just a plan that got approved.
jaggedben
If it's a PV array without optimizers then it's very similar to a battery bank. If you have a separate rapid shutdown switch or DC disconnect then not so much.
tortuga
Exactly then 110.26(A) would apply.
In this situation we have a DC disconnect before the inverter, it would be another discussion if the rapid shutdown switch would qualify as a DC disconnect.
PV Array -> DC fused disconnect / AFCI -> Inverter (no overcurrent devices here) -> AC circuit breaker.
pv_n00b
I know plenty of AHJs who would fail this installation based on 110.26. Good thing you got lucky and the AHJ for this project decided to accept it, it shows that it never hurts to ask. Don't assume that now you are free and clear to do this anywhere else though.