Hi all,
Doing a solar PV install in California, and have a question about grounding (GEC + EGC).
The house is a typical 1980s style build. I'm not sure where the existing ground ties to, but I'm assuming it's the water line.
The PV install in question consists of Enphase microinverters (DC -> 240VAC at a per-panel level), on aluminum racking. The proprietary 2-conductor Enphase 240VAC cable lands in a metal roof-mounted junction box (Soladeck), and feeds down to the Enphase Combiner through EMT.
The microinverters are ungrounded / double-insulated. Therefore the only grounding of note is the railing (on the roof).
This is done with #6 between rails, with ironridge grounding lugs, to the Jbox. Inside the Jbox, there is a ground bar, on which the #6 from the rails, and a #10 THHN which feeds back to the combiner, and a wire from a grounding bushing on the EMT all land. This EMT feeds into the Enphase Combiner box on the side of the house.
1. According to the AHJ inspector, using a ground terminal block inside the jbox on the roof is not acceptable, and they need to be irreversibly spliced together. Is this true? Any code I can quote to the contrary? Isn't this a GEC requirement rather than a EGC requirement?
2. My plan is to add two grounding rods (obv, irreversibly spliced here), 6ft+ apart, to satisfy current code, and land that in the existing SE panel, which has a ground terminal block. The Enphase Combiner (physically next to the service entrance), then has a grounding conductor also land on that terminal block. Do I need two, or can the existing water pipe bond count as one of the two (assuming I'm not ohming it out for the <25-ohm single rod req)?
Ref:
Doing a solar PV install in California, and have a question about grounding (GEC + EGC).
The house is a typical 1980s style build. I'm not sure where the existing ground ties to, but I'm assuming it's the water line.
The PV install in question consists of Enphase microinverters (DC -> 240VAC at a per-panel level), on aluminum racking. The proprietary 2-conductor Enphase 240VAC cable lands in a metal roof-mounted junction box (Soladeck), and feeds down to the Enphase Combiner through EMT.
The microinverters are ungrounded / double-insulated. Therefore the only grounding of note is the railing (on the roof).
This is done with #6 between rails, with ironridge grounding lugs, to the Jbox. Inside the Jbox, there is a ground bar, on which the #6 from the rails, and a #10 THHN which feeds back to the combiner, and a wire from a grounding bushing on the EMT all land. This EMT feeds into the Enphase Combiner box on the side of the house.
1. According to the AHJ inspector, using a ground terminal block inside the jbox on the roof is not acceptable, and they need to be irreversibly spliced together. Is this true? Any code I can quote to the contrary? Isn't this a GEC requirement rather than a EGC requirement?
2. My plan is to add two grounding rods (obv, irreversibly spliced here), 6ft+ apart, to satisfy current code, and land that in the existing SE panel, which has a ground terminal block. The Enphase Combiner (physically next to the service entrance), then has a grounding conductor also land on that terminal block. Do I need two, or can the existing water pipe bond count as one of the two (assuming I'm not ohming it out for the <25-ohm single rod req)?
Ref:
PV enphase microinverter
Does IQ7-60-2-US micro inverter 240V single phase require neutral brought to them? Anyone have manufacturer datasheet or instruction that says neutral is not required?