kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
You must have a supply side neutral for your GFCI. What you don't need is a neutral run out with load conductors if there is no neutral load to be served. That supply side neutral powers the GFCI electronic circuitry. If you don't hook it up you have no GFCI protection and effectively turn your $100+ GFCI 2 pole breaker into a standard thermal magnetic breaker, which might only be a $20-30 item depending on which brand is involved.Would it be possible to use a spa disconnect and wire it 240v and install the GFCI breaker in it? Obviously there wouldn't be a neutral but if it's only used for the 240v irrigation pump would this be code compliant?