correct Table 240.6(A) shows 50 or 60 Amp as standard, but wire still must be protected at not more than its max rating. So #6 NM is rated for not more than 55A(Side note: I learned in this thread that a 55A breaker is a thing. But it's still not a standard ampere rating!)
Tesla recognition of the limitation of NM and the equipment requires a 60A overcurrent protection and NM is only good for 55A. Rather than rely on the unskilled deciphering of the code, they bypass this by just dictating the specific wire. THWN-2 gives the 60A under most installation conditions both inside and outside of structures by exceeding the 60A required with a 75A rated conductor. This instruction by Tesla make the installation a 110.3(B) requirement.Why does Telsa explicitly says to use TWHN-2?