Is a bare EGC permitted in RNC?
Are you going after the dissimilar metals angle?
Roger
Well, I'm trying to understand why a specific wiring method was singled out in the thread mentioned in my OP. If all wiring methods in the list can contain uninsulated EGCs, then why is AC special in Article 518?
I wasn't when I first brought it up, but I wouldn't mind discussing it again. For example, Rick mentioned that angle in the other thread; instinctively, we believe such a rule exists when in reality I don't think it does.
It depends on how someone interprets and/or applies 358.12(6) or the 3xx.14 sections.
Roger
That is perfect! I don't see how it could be applied any other way, unless we take it for granted that EGCs will not under any circumstances be conducting current in other than fault conditions. :cool:
Thanks for that, Roger!
Anyone disagree?
I recommend the EGC in conduit, metal or not, be insulated, as in a ground fault it will get hot and could damage the adjacent conductors.
Doesn't the heating require more time than the protective device is supposed to allow? After all, look how small some EGC's may be compared to the corresponding circuit conductors.