Is a Bonding Bushing required?

Status
Not open for further replies.

zinsco

Member
Location
San Diego, CA
Installing a 100 amp 3ph 120/208v panel. Running emt from a 6 meter section at the switchgear to suit 100a. My panel does have concentrics, but since it is not over 250v am I correct in believing that it will not require a bonding bushing?
 
Installing a 100 amp 3ph 120/208v panel. Running emt from a 6 meter section at the switchgear to suit 100a. My panel does have concentrics, but since it is not over 250v am I correct in believing that it will not require a bonding bushing?

As long as it is a feeder and not service conductors you are correct.
 