Re: Is a buck transformer needed ???
Thats correct too bennie . When overheasting occurs torque begins to drop and if the load remains the same overheating will continue and deteriorate the winding insulation and as a matter of fact if the heat continues to build and if the load is not reduced complete failure will occur. The paragraph you quote is a warning that you really should not run a motor fully loaded at a 10% drop in nameplate voltage however the NEMA standard for motors allows this to happen they just dont reccomend it. Neither do I. Owned my own electric motor shop for nearly 20 years and the engineers who used the service factor voltage were my freinds. Kept us in the rewind and replacement business!!!
Thats correct too bennie . When overheasting occurs torque begins to drop and if the load remains the same overheating will continue and deteriorate the winding insulation and as a matter of fact if the heat continues to build and if the load is not reduced complete failure will occur. The paragraph you quote is a warning that you really should not run a motor fully loaded at a 10% drop in nameplate voltage however the NEMA standard for motors allows this to happen they just dont reccomend it. Neither do I. Owned my own electric motor shop for nearly 20 years and the engineers who used the service factor voltage were my freinds. Kept us in the rewind and replacement business!!!