Is a ground bar considered a bus bar?

Status
Not open for further replies.

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I agree with Dennis. His pic shows what I call a small busbar, and the neutral or grounding bar in a typical panel I call just a bus.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
And for more.


Listed under UL 467

Roger
 

Epalmateer

Senior Member
Location
Michigan
Occupation
Electrician
And for more.


Listed under UL 467

Roger
Hell yeah. I need to put in a PI about this
 

Epalmateer

Senior Member
Location
Michigan
Occupation
Electrician
Why? They are already identified under a UL. classification, they don't need a anything else

Roger
Idk. Maybe I misinterpreted your text. If you were an inspector, would you allow the gec to be extended inside of a panel by means of the ground bar?
 

rambojoe

Senior Member
Location
phoenix az
Occupation
Wireman
But without definitions or rules, could you see how someone could argue that a ground bar is a busbar?
Its up to the manufacturer in list of equipment/gear parts to first call it what THEY wanna call it...
Edit, it sounds like you want to add...
 