I am working on a project that is providing building level battery backup. The battery backup system utilizes a 480 V delta inverter that operates without a neutral. I was instructed by the manufacturer to provide a neutral forming transformer on the output of the inverter so the battery backup system can provide power to 277 L-N loads during backup mode. So I am currently planning for a 480 Delta (Inverter side) to 480/277Y (grid side) transformer.
My question, if there is a ground fault on the inverter side of the transformer, is this safe? How will a ground fault clear if there is no neutral for a N-G bond?