Coppersmith
Senior Member
- Location
- Tampa, FL, USA
- Occupation
- Electrical Contractor
I have been asked to install the wiring for a 20Kw generator at a residence with a 320 amp service and two 150 amp MB panels back-to-back with meter. They are supplying two 200 amp non service rated ATS's.
If I insert an ATS between the meter and each panel, do the ATS's have to be service rated? I think I will be able to keep the feeders very short. My jurisdiction requires a main breaker by the meter if the feeder is more than 5 feet long. However, seems like I would need a service rated ATS just so I could simulate a power outtage for test purposes.
Secondly, Since the service is 320 amps, would 200 amp non service rated ATS's be OK? What if they were 200 amp service rated?
As an interesting aside, the UG conduit going into the meter can is 2" PVC. It's a 320 amp meter can, but I'm wondering if it's really being fed with a 320 amp service. I know the POCOs tend to undersize their wires, but I usually see 3" conduit for 320/400 amp services.
If I insert an ATS between the meter and each panel, do the ATS's have to be service rated? I think I will be able to keep the feeders very short. My jurisdiction requires a main breaker by the meter if the feeder is more than 5 feet long. However, seems like I would need a service rated ATS just so I could simulate a power outtage for test purposes.
Secondly, Since the service is 320 amps, would 200 amp non service rated ATS's be OK? What if they were 200 amp service rated?
As an interesting aside, the UG conduit going into the meter can is 2" PVC. It's a 320 amp meter can, but I'm wondering if it's really being fed with a 320 amp service. I know the POCOs tend to undersize their wires, but I usually see 3" conduit for 320/400 amp services.