To qualify as a chapter 3 wiring method it must be continuous from "box to box". Conductors pulled inside would need to be from 310 also. flexible cord is not covered in 310.Can penetrations be sleeved with PVC to qualify as a chapter 3 wiring method between floors?
Dishwasher has some specific allowances in 422.16, basically it can have the receptacle in adjacent space to the appliance itselfI agree, so it depends. Does this dishwasher have a line cord usually secured with a Romex connector going into a J box or wiring compartment? Then you certainly can remove it. However, if the line cord goes directly into the appliance with no way to get at it then you consider it permanently attached.
It's been awhile, but I never saw a DW with a line cord. Usually I would bring the supply up through the floor, put a 1900 box on it with a disconnect switch and from there to the DW. That way you can remove the bottom DW panel and reach in to get at the switch. The 1900 box isn't fastened to anything so the DW can be slid into place.
NOPE!! Flexible cords cannot pass through floors or walls, period.
-Hal
That could be brilliant for inspectors who deliberately check for a disconnect, but I doubt many of them are checking for it...I would bring the supply up through the floor, put a 1900 box on it with a disconnect switch and from there to the DW. That way you can remove the bottom DW panel and reach in to get at the switch. The 1900 box isn't fastened to anything so the DW can be slid into place.
But they're not one of the items listed under (A)(1) through (5). Anyhow, the point that I was trying to make is that hard-wired stuff still needs AFCI in this case.The last I knew, dishwashers were appliances. Refer to 422.5(A).
If you are under the 2020
The gfci can be anywhere in the house so long as its 'readily accessible', even though I am use to seeing it close by. Is there reason why the dishwasher cannot be hardwired behind it and have enough flex or romex to be able to move it out? Or what about installing the (gfci?)receptacle under a sink in the kitchen and having a cut out for the cord to pass through the cabinet sides? assuming the dishwasher is installed right by a sink. (cabinets sides are not walls so there is no nec violation as far as I know),
....(7) Dishwashers.But they're not one of the items listed under (A)(1) through (5). Anyhow, the point that I was trying to make is that hard-wired stuff still needs AFCI in this case.
That number (7) is not in the 2017....(7) Dishwashers.
As I see the original install with the receptacle in an unfinished basement, the AFCI is not required. The GFCI is.
Moot points anyway. It wasn't a legal install to begin with so now it should be brought to whatever current code is for the area.