DavidWalton
Member
- Location
- Lake Jackson TX
I am in the process of updating our city ordinances to adopt the 2015 I Codes and make necessary changes to our amendments. I need an honest fact based answer to the question regarding use of aluminum wiring in areas with corrosive atmospheres. We are on the Texas Gulf Coast and in a Hurricane prone area.
Our current ordinance reads:
(4) Any and all codereferences permitting or requiring aluminum wire shall not be applicable,except when used as an option in underground service to the electric utilitymeter or when all of the following requirements are met: (a) The building consists of at least 3 storiesor 75,000 sq. ft.;
· (b) The building electrical service from theutility provider is480Y/277V, 3 phase, 4 wire;
(c)· The building has a main service of1600 Amps or larger;
(d)· The building Main Service DisconnectingMeans is of Switchboard Construction. (Buildings served with Gutter andDisconnect Switch configurations will not be permitted to use above groundaluminum feeders.);
(e) All aluminum conductors are compression type conductors and use penetroxwith compression termination fittings;
(f)· The electrical contractor providesthe number of lugs and proper lug sizes to accept the larger aluminum conductorsizes required;
(g)· Aluminum feeders are not used toserve chillers, elevators or equipment utilizing variable frequency drives;
(h)· Aluminum conductors are not used onthe secondary side of step down transformers; and
(i)· Aluminumconductors are only to be used on feeders that are 200Amps and larger.
I want to redact this prohibition for the following reasons.
Can someone point me to research or data that would justify the prohibition? Our former BO did quite a bit of shooting from the hip and based decisions upon personal preference and prejudice.
Your help is greatly appreciated.
Our current ordinance reads:
(4) Any and all codereferences permitting or requiring aluminum wire shall not be applicable,except when used as an option in underground service to the electric utilitymeter or when all of the following requirements are met: (a) The building consists of at least 3 storiesor 75,000 sq. ft.;
· (b) The building electrical service from theutility provider is480Y/277V, 3 phase, 4 wire;
(c)· The building has a main service of1600 Amps or larger;
(d)· The building Main Service DisconnectingMeans is of Switchboard Construction. (Buildings served with Gutter andDisconnect Switch configurations will not be permitted to use above groundaluminum feeders.);
(e) All aluminum conductors are compression type conductors and use penetroxwith compression termination fittings;
(f)· The electrical contractor providesthe number of lugs and proper lug sizes to accept the larger aluminum conductorsizes required;
(g)· Aluminum feeders are not used toserve chillers, elevators or equipment utilizing variable frequency drives;
(h)· Aluminum conductors are not used onthe secondary side of step down transformers; and
(i)· Aluminumconductors are only to be used on feeders that are 200Amps and larger.
I want to redact this prohibition for the following reasons.
- 2014 NEC does not limit the use of aluminum wiring along coastlines.
- NEC provides installation requirements for aluminum wiring systems.
- Our ordinance lists specific products to be used at installation.
- This could provide savings to the building owners.
Can someone point me to research or data that would justify the prohibition? Our former BO did quite a bit of shooting from the hip and based decisions upon personal preference and prejudice.
Your help is greatly appreciated.