muskiedog said:How is the room a part of the egress? leading to the exit? The key word is from
jack horner said:No. Not required
Ragin Cajun said:As I do design for "conference" rooms, I tend to play it on the safe side. A bug eye, fluorescent battery pack, etc. on the plans is in the grand scheme of things cheap, ~<$100. BUT, get some inspector, FD, etc. with a wild hair who wants it AFTER the fact and you're looking at $2-300 and a ticked off client.
Per OSHAllverbeek said:every part of every building is part of the means of egress...
If you consider the whole building a means of egress you would not be able to place anything in it.
gosh, raider.. why do you think the building codes have "travel distance"... it's to an EXIT..
I see you have solved the problem, but when it comes up again, Bodine has relays to allow you to switch the night light.mike9999 said:If I connect emergency night light in the conference room then there is no way I can turn it off for video presentation.
1003.2.11 Means of egress illuminations. The means of egress, including the exit discharge shall be illuminated at all times the building space served by the means of egress is occupied"....
1006.3 Illumination emergency power. The power supply for
means of egress illumination shall normally be provided by the
premises? electrical supply.
In the event of power supply failure, an emergency electrical
system shall automatically illuminate the following areas:
1. Aisles and unenclosed egress stairways in rooms and
spaces that require two or more means of egress.
2. Corridors, exit enclosures and exit passageways in buildings
required to have two or more exits.
3. Exterior egress components at other than the level of exit
discharge until exit discharge is accomplished for buildings
required to have two or more exits.
4. Interior exit discharge elements, as permitted in Section
1024.1, in buildings required to have two or more exits.
5. Exterior landings, as required by Section 1008.1.5, for
exit discharge doorways in buildings required to have
two or more exits.
The emergency power system shall provide power for a
duration of not less than 90 minutes and shall consist of storage
batteries, unit equipment or an on-site generator. The installation
of the emergency power system shall be in accordance
with Section 2702.
steve66 said:I think Radier has it right.
If you are going to require a emergency light in a conference room that doesn't need two exits, then every single room in the building would need an emergency light. Never had a building official require that.
Steve
sparkie001 said:Bodine has relays to allow you to switch the night light.