Is an outdoor spa a seperate structure?

Status
Not open for further replies.
Re: Is an outdoor spa a seperate structure?

See the exception to 250.32(A):
Exception: A grounding electrode at separate buildings or structures shall not be required where only one branch circuit supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the conductive non?current-carrying parts of all equipment.
 
Re: Is an outdoor spa a seperate structure?

Originally posted by george t. everett:
Does a light pole require a grounding electrode?
I think not.
Yes it does require a grounding electrode if it is served by a feeder or more than one branch circuit. ;)
 