I find the NEC a little complicated when trying to figure out how many #14 THNN 90 degree MYW wires are allowed in a 1/2" EMT conduit on a 15 amp general purpose circuit for lighting.
I read the 358.22, and based on Chapter 9 table 5, I found the #14 THHN has .0097in2 and with the ?? EMT conduit having a .304in2 total area, the 40% fill rule would allow me .304*.4/.0097 = 12 wires. So far so good...
For a 15A light breaker circuit, would I need to concern myself with chapter 310, in particular 310.15 ampacity calculations? The posts I found so far looked like only 358.22 were used?
I read the 358.22, and based on Chapter 9 table 5, I found the #14 THHN has .0097in2 and with the ?? EMT conduit having a .304in2 total area, the 40% fill rule would allow me .304*.4/.0097 = 12 wires. So far so good...
For a 15A light breaker circuit, would I need to concern myself with chapter 310, in particular 310.15 ampacity calculations? The posts I found so far looked like only 358.22 were used?