505.2 Lighting controls. (Mandatory). Lighting systems
shall be provided with controls as required in Sections 505.2.1,
505.2.2 , 505.2.3 and 505.2.4.
505.2.1 Interior lighting controls. Each area enclosed by
walls or floor-to-ceiling partitions shall have at least one
manual control for the lighting serving that area. The
required controls shall be located within the area served by
the controls or be a remote switch that identifies the lights
served and indicates their status.
Exceptions:
1. Areas designated as security or emergency areas
that must be continuously lighted.
2. Lighting in stairways or corridors that are elements
of the means of egress.
505.2.2 Additional controls. Each area that is required to
have a manual control shall have additional controls that
meet the requirements of Sections 505.2.2.1 and 505.2.2.2.
505.2.2.1 Light reduction controls. Each area that is
required to have a manual control shall also allow the
occupant to reduce the connected lighting load in a reasonably
uniform illumination pattern by at least 50 percent.
Lighting reduction shall be achieved by one of the
following or other approved method:
1. Controlling all lamps or luminaires;
2. Dual switching of alternate rows of luminaires,
alternate luminaires or alternate lamps;
3. Switching the middle lamp luminaires independently
of the outer lamps; or
4. Switching each luminaire or each lamp.
Exceptions:
1. Areas that have only one luminaire.
2. Areas that are controlled by an occupant-sensing
device.
3. Corridors, storerooms, restrooms or public lobbies.
4. Sleeping unit (see Section 505.2.3).
5. Spaces that use less than 0.6 watts per square
foot (6.5 W/m2).