Is EMT Considered an Intermediate Conduit or Not

Status
Not open for further replies.

smiller24

New member
I am installing a pool and have used EMT as an Electrical Conduit from the house to an above ground pool. It is buried 18 inches in the ground. I have been told by an electrical inspector that this is not considered an intermediate conduit and not to code. Can I use EMT as an Intermediate Conduit or not. It seems like it is a 'gray' area in the NEC. If someone sees this please let me know. Thank you.
 
The inspector is correct, there is no gray area.

RMC is Rigid Metal Conduit

RNC is Rigid Non-metallic Conduit

IMC is Intermediate Metal Conduit


But EMT is Electrical Metallic Tubing

Tubing is not Conduit.


Considering you, your families and your friends safety is in the balance you should hire a electrician to do this work.
 
480sparky said:
Try reading the definition of a raceway. Especially the second sentence.

You lost me. :-?

Raceways include pretty much everything.

Conduits and Tubings are both examples of raceways.
 
smiller24 said:
I am installing a pool and have used EMT as an Electrical Conduit from the house to an above ground pool. It is buried 18 inches in the ground. I have been told by an electrical inspector that this is not considered an intermediate conduit and not to code. Can I use EMT as an Intermediate Conduit or not. It seems like it is a 'gray' area in the NEC. If someone sees this please let me know. Thank you.

Did you do this at your house?
Is was it coverd yet?
 
iwire said:
You lost me. :-?

Raceways include pretty much everything.

Conduits and Tubings are both examples of raceways.

Then you got it.

All sedans are vehicles, but not all vehicles are sedans.
All Americans are human beings, but not all human beings are Americans.
All Macs are PCs, but not all PCs are Macs.

Ad nauseum, ad infinitum.

"Raceways" is an all-encompassing term. "Conduits" and "Tubing" are smaller groups within that 'family' of raceways.
 
Last edited:
I'm sure the OP will hire an Electrian now, after that fine display of defining

what a pipe is called. Was that the important message , or was it that this

guy should not be wiring a swimming pool ?

I know, If you don't like it don't read it. I guess it's my problem !
 
Gee where are the mod's ?

Gee where are the mod's ?

Occupation:
network tech
How are you related to the electrical industry?:
network cable installation

:cool: :cool: :cool:
 
acrwc10 said:
Occupation:
network tech
How are you related to the electrical industry?:
network cable installation

:cool: :cool: :cool:
A square is a rectangle. But a rectangle is not a square.
An electrician is a network cable installer. But a network cable installer is not an electrician.
 
JES2727 said:
A square is a rectangle. But a rectangle is not a square.
An electrician is a network cable installer. But a network cable installer is not an electrician.

Unless he is putting EMT underground to a pool :D
 
JES2727 said:
A square is a rectangle. But a rectangle is not a square.
An electrician is a network cable installer. But a network cable installer is not an electrician.

You men are funny.

I'd rather give up the morning comics and coffee than this forum . . .

Best Wishes Everyone
 
acrwc10 said:
Unless he is putting EMT underground to a pool :D

And then he becomes a hazard. :D

The wheels came off this rig in post 3 ,..

Remember ,..a square is a polygon
yet ,..not all polygons are square
 
Smiller24, you really should hire an electrician for this.