Is gas pipe being used as electrode

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have metal gas pipe bonded to service panleboard ground bus. The metal pipe right where bonding jumper is has grounding electrode conductor with ground rods. By putting that grounding electrode conductor am I not using metal gas pipe as grounding electrode?
 
This might help to explain.
 

Attachments

  • Your Safety Is Our Priority - Information Inside.pdf
    992.8 KB · Views: 2
  • Electrical Grounding Safety #1.jpg
    Electrical Grounding Safety #1.jpg
    805.4 KB · Views: 8
  • Electrical Grounding Safety #2.jpg
    Electrical Grounding Safety #2.jpg
    1.2 MB · Views: 8
  • Electrical Grounding Safety #3.jpg
    Electrical Grounding Safety #3.jpg
    914.1 KB · Views: 8
NEC (National Electric Code) Section 250.52(B)(1) ... Not permitted for Use as Grounding Electrodes:
The following systems and materials shall not be used as grounding electrodes:
1) Metal underground gas piping system
2) Aluminum
 
However,
since the metal gas piping inside of the home could
inadvertently become energized, each aboveground
portion of a gas-piping system upstream from the
equipment shutoff valve shall be electrically continuous
and bonded to the grounding electrode system,
Section 250-104(b).
 
So then in my case metal gas pipe is grounding electrode?

Also, sheet metal screws are not permitted to be used
as a means of connecting grounding conductors to
enclosures, Section 250-8. Sheet metal screws do not
have the same fine thread that 10/32 machine screws
have, which match the tapped 10/32 threaded holes
in outlet boxes, device boxes, and other enclosures.
 
Most utilities have a di-electric fitting that isolates the underground gas line from the above ground. If it is bonded to the line side of the gas meter then that would be non-compliant.
 
And new gas piping installed by gas companies us non metallic HDPE. There is a dialectric union at the gas meter for metal gas piping. Gas company does not want electrical bonded to their piping as it interferes with cathodic protection
 
The metal pipe right where bonding jumper is has grounding electrode conductor with ground rods. By putting that grounding electrode conductor am I not using metal gas pipe as grounding electrode?
The gas pipe it self cant be part of the ground fault path, you cant use it like a ground bar. so you cant have a say a #6 from a ground rod to a clamp on a gas pipe then a 2nd clamp on the gas pipe with a GEC to a water pipe, then a 3rd GEC from gas pipe to the service.
You can have a have a continuous unspliced loop of bare copper that hits the water pipe, ground rods and gas pipe.
 
The gas pipe it self cant be part of the ground fault path, you cant use it like a ground bar. so you cant have a say a #6 from a ground rod to a clamp on a gas pipe then a 2nd clamp on the gas pipe with a GEC to a water pipe, then a 3rd GEC from gas pipe to the service.
You can have a have a continuous unspliced loop of bare copper that hits the water pipe, ground rods and gas pipe.

This might help to explain.
 

Attachments

  • Electrical Wiring Residential - Gas Pipe Bonding.pdf
    126.9 KB · Views: 6
This might help to explain.
I believe this depicts what the op is asking about, a GEC that hits a water main then a gas main then other metal pipes, in any order.
This is a more up to date diagram of what grounding and bonding should be inspected by an AHJ such as @hhsting when a EC pulls a permit that includes upgrading the grounding electrode system in the scope, such as a typical residential service change. All the elements of the grounding system should be evaluated and it should be verified new and old systems are bonded.

Residential-service_Bonding.png
 