Matt Donovan
- United States
I have a 480Vac PV system connected to a 208V service, so we are using a step-up transformer between the PV disconnect and the existing main switchgear. This is a load-side interconnection, and the existing gear has a GFCI main, so normally I would need to use a GFCI breaker for the interconenction, per 705.32. But does the transformer prevent ground fault current from flowing from secondary to primary? If so, then my PV system does count as a ground fault current source to the existing switchgear, and I should not need a GFCI on the PV breaker. The transformer is is delta primary (utility side) :: wye-G secondary (PV-side).