I'm working under 2014 NEC. I'm looking at section 680, but I must be missing it. This is a 50 or 60 amp heater. GFCI required?
Is this a heatpump type heater?
I know I don't agree with the code on this.Not required. I don't know that I agree with it,
Nec 2017 said:680.28 Gas-Fired Water Heater. Circuits serving gas-fired
swimming pool and spa water heaters operating at voltages
above the low-voltage contact limit shall be provided with
ground-fault circuit-interrupter protection for personnel.
Yes 210.8(F)We just installed a 50 amp gfci on a heat pump pool water heater. Is that required for NEC 2020 ?
Yes 210.8(F)
This code change came as a result of a child’s death. On August 3, 2007, a 12-year-old child jumped over a chain link fence and landed on the adjacent AC condenser unit. The condenser had an electrical ground fault which caused the unit's metal housing to become electrified. The child was fatally electrocuted when he made contact simultaneously with both the condenser and the metal fence.