Well, what is required resistance to ground is 25 ohms or less, right? Break out the megger and see what you have. I thought it is required along with bonding building steel and water pipe, but the ufer is the thing in question...I'll check and I shall return with an answer.
You may use 1 rod if the rod resistance is 25 ohms or less as the GES. If not, 2 rods properly spaced are required. No further measurement is required by the NEC. A rod supplementing any other electrode does not need to be tested. A Ufer does not requre testing by the NEC.