Rebar grids in slabs are not required to be bonded. They are not “likely to become energized”.
A CEE (concrete encased electrode) is a different thing entirely. The NEC now requires 20’ of 1/2” rebar, OR, 20’ of #4 solid copper wire, to be embedded in a *footing or foundation*, if the concrete is in contact with earth, and to be used as the grounding electrode.
“In direct contact with earth” is key here. The building code requires all heated structures to have a 10 mil vapor barrier below slabs. Some residential, and even commercial buildings, will have insulated slabs, especially if they have radiant floor heating. As both vapor barriers and polyisocyanurate foam board insulation, which is used in insulated slabs, break the direct contact with earth, the CEE is virtually never used in new slab-on-grade construction.