This is an area that takes a really good understanding of grounding. For now, I'm going to avoid direct comment and instead direct you to:The problem with just calling it a "PV System Disconnect" is some may think the disconnect would not need important safety features such a grounded conductor connection to the disconnect switch...or a main bonding jumper. If it is not a AC supplied service then those are not required...right.
a) Information Notes No. 1 & 2 of 690.47(C),
b) 250.6, and
c) a general comment that bonding a grounded conductor at more than one point creates a path for objectionable current.
So if you call the disconnect of contention a Service Disconnect, you have a load side connection and size the feeder to the 120% rule?Any supply side connected PV System would still be subject to the 705.12...both supply side and load side.
If this power was not supplied directly through the PV System disconnect, it would be covered under 230.82(4), (5), (7), or (9).It is a Service. Inverters use power...data acquisition systems use power, all supplied to the premises wiring system by the serving utility. Without Service a Grid Tied PV system will not work.