jot30 said:When installing an auto-transfer generator, per nec, is it acceptable to use wire nuts in the service panel, to make circuit connections to the new generator transfer panel?
jot30 said:When installing an auto-transfer generator, per nec, is it acceptable to use wire nuts in the service panel, to make circuit connections to the new generator transfer panel?
peter d said:Yes.
It is easier to pass a camel through the eye of a needle than it is to violate the code section (312.8) that addresses splices in gutter space in your average residential load center.
peter d said:Yes.
It is easier to pass a camel through the eye of a needle than it is to violate the code section (312.8) that addresses splices in gutter space in your average residential load center.
JohnJ0906 said:Getting biblical on us, Peter? :grin:
jot30 said:Thanks for the help...Inspector had different take!
God Bless.
jot30 said:I meant it!..... The God Bless too! The inspector told us we were using the service panel as a JB. "a clear violation" So thanks for the code help.