Is it acceptable to use wire nuts in the service panel?

Status
Not open for further replies.

jot30

Member
Occupation
Electrician/Electrical Inspector
When installing an auto-transfer generator, per nec, is it acceptable to use wire nuts in the service panel, to make circuit connections to the new generator transfer panel?
 
jot30 said:
When installing an auto-transfer generator, per nec, is it acceptable to use wire nuts in the service panel, to make circuit connections to the new generator transfer panel?


Yes, not a problem at all.
 
jot30 said:
When installing an auto-transfer generator, per nec, is it acceptable to use wire nuts in the service panel, to make circuit connections to the new generator transfer panel?

Yes-- read art. 312.8 but don't stop at the first sentence. ;)
 
Yes.

It is easier to pass a camel through the eye of a needle than it is to violate the code section (312.8) that addresses splices in gutter space in your average residential load center.
 
peter d said:
Yes.

It is easier to pass a camel through the eye of a needle than it is to violate the code section (312.8) that addresses splices in gutter space in your average residential load center.


Which one did you do? :grin:
 
peter d said:
Yes.

It is easier to pass a camel through the eye of a needle than it is to violate the code section (312.8) that addresses splices in gutter space in your average residential load center.

Getting biblical on us, Peter? :grin:
 
Is it acceptable to use wire nuts in the service panel?

Thanks for the help...Inspector had different take!

God Bless.
 
Regarding...Thanks for the help...Inspector had different take!

Regarding...Thanks for the help...Inspector had different take!

I meant it!..... The God Bless too! The inspector told us we were using the service panel as a JB. "a clear violation" So thanks for the code help.
 
jot30 said:
I meant it!..... The God Bless too! The inspector told us we were using the service panel as a JB. "a clear violation" So thanks for the code help.

Yep, the violation was a clear as mud.:D

Glad you got this cleared up with the inspector.

Chris
 