Hello gang, I have a customer that ran a 12/3 UF to a shed, I typically run a minimum of 10/3 but this is now installed and buried.
I realize I could install a 2 pole switch but I was planning on installing a 4 spot main lug panel with 3 breakers 20,20 and 15, so lights and equipment are not on one GFCI breaker. Is it legal to have a 20A feeder to 3 circuits? The main breaker at the building is a 2-pole 20. And if so can I run a #12 to the ground rods?
Thank you
I realize I could install a 2 pole switch but I was planning on installing a 4 spot main lug panel with 3 breakers 20,20 and 15, so lights and equipment are not on one GFCI breaker. Is it legal to have a 20A feeder to 3 circuits? The main breaker at the building is a 2-pole 20. And if so can I run a #12 to the ground rods?
Thank you