If there is a panel in the shed then the condcutors feeding it are a feeder not a MWBC.
Start reading at 225.31 as that tells you all about the disconnecting means for the detached building. It is not a feeder disconnect, it is a building disconnect. A key is subpart (B) Location. The disconnect needs to be at the remote building, nearest the point of entry of the conductors.Thanks again for your input, the disconnect of the feeder where is where it begins no? It starts from a 2 pole 20 in the main building. If I shut off the breaker at the end of the feeder I have not disconnected it, its still on.
Yes and they are planning on clarifying that for the 2026, I think there were a few proposals to change the wording to the disconnect required by 225.31.Start reading at 225.31 as that tells you all about the disconnecting means for the detached building. It is not a feeder disconnect, it is a building disconnect. A key is subpart (B) Location. The disconnect needs to be at the remote building, nearest the point of entry of the conductors.
I think he could do a #8 as thats the minimum in 250.66.6 to ground rod, rods.
Could be. 6 in the largest it has to be but i believe 8 requires protectionI think he could do a #8 as thats the minimum in 25250.66.