Is it ok to have 2 disconnects 230v and 460v in one panel?

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Could you explain more of the situation. I am having a hard time understanding 2 disconnects of different voltages in a panel.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
If you have multiple sources of power coming into a panel, one at 480V and one at 240V, you would be REQUIRED to have two disconnects in most cases. but if the source for the 240V is a transformer powered by the same 480V disconnect and attached to the panel, then another disconnect may not be necessary.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
Make sure that the voltage class of the lower voltage operated equipment (240V) is rated for at least 480V. In general, if that is the case, should not be an issue.
 