Is It Required...

Status
Not open for further replies.

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
Set up:

Daycare/Pre-School Bathroom, sink & toilet
Water Fountain
His & Her Water Closets, toilet w/exhaust fan, ceiling light & duplex receptacle in each.

Currently all of the above are controlled by the GFI in the Bathroom

Question:

Is GFI protection required for the Water Closets?

I have looked at 2014 210.8 (B) and I conclude No.
 
Set up:

Daycare/Pre-School Bathroom, sink & toilet
Water Fountain
His & Her Water Closets, toilet w/exhaust fan, ceiling light & duplex receptacle in each.

Currently all of the above are controlled by the GFI in the Bathroom

Question:

Is GFI protection required for the Water Closets?

I have looked at 2014 210.8 (B) and I conclude No.

What is a water closet?

It sure sounds like a bathroom

From article 100
Bathroom. An area including a basin with one or more of
the following: a toilet, a urinal, a tub, a shower, a bidet, or
similar plumbing fixtures.
 
Yes, son of a plumber here and yes he would call a toilet a water closet but it sounded like the OP was treating water closets as a room.

Yes, I'm calling a room with only a toilet, no basin, a Water Closet, could not think of any other descriptor for this room.
 
So you have one room with a sink that is connected to two other rooms with toilets?

Nope, one full bathroom.

In another area are two classrooms that have room(s) with just a toilet. The sink, basin, for washing hands is outside of the toilet room(s).
 
Nope, one full bathroom.

In another area are two classrooms that have room(s) with just a toilet. The sink, basin, for washing hands is outside of the toilet room(s).

So you're asking if the toilet rooms need GFCI protection?
 
Nope, one full bathroom.

In another area are two classrooms that have room(s) with just a toilet. The sink, basin, for washing hands is outside of the toilet room(s).

I am confused as I was under the impression building or health codes require a sink with a toilet.
 
In my area, plumbing codes have changed to require the sink in the same space as the toilet. Previously, a popular school design was to place the sinks outside the toilet space so the students could be monitored.
 
The NEC does not require anything in that space.

If the room only has a toilet it is not a bathroom to the NEC.

Even if it is a "bathroom" it's in a non dwelling unit, therefore not requiring a receptacle. But....if there is a receptacle, I think it would need GFCI protection.
 
Need Further Info

Need Further Info

Is this Daycare in a one or two family home?
Are there receptacles required?
Commercial building = none required.
Water closet = bathroom with receptacle = GFCI right?
Despite all of the above, within 6 ft. of a sink = GFCI
In an area frequently occupied by children with water, this is a no-brainer. GFCI
Am I missing something here?
 
Is this Daycare in a one or two family home?
Are there receptacles required?
Commercial building = none required.
Water closet = bathroom with receptacle = GFCI right?
Despite all of the above, within 6 ft. of a sink = GFCI
In an area frequently occupied by children with water, this is a no-brainer. GFCI
Am I missing something here?

Tamper Resistant.
 
Last edited:
No offense intended but please don't say "Tamper-proof."
As an inspector, I hear that all day.
It's "Tamper resistant."
And I agree that TR is required.
Sorry, that's like hearing "Carbon Dioxide" detector.
And....nothing is "anything proof."
To quote an old saying: "If you 'Idiot Proof' something, they'll just adapt better idiots.":)
 