So I guess I have a few questions.
I specified that our MV SWGR be 63KAIC. The vendor does not offer 63 KAIC but offers 50 KAIC. The vendor than comes back with a method to attain 25 KAIC by the use of these Is limiters. They are to be connected at each end of the SWGR to the main circuit breakers.
1. Why would I use these Is limiters when I want 63 KAIC rather than a lower KAIC?
2. It states it is only connected to the main circuit breakers what about the feeder breakers? If the limiters are just connected to the main breakers, the feeder breakers would still be 50 kAIC?
3. Does anybody have experience with these Is limiters? Do I want to have a smaller KAIC? is it more economical?
I know these are questions to the vendor, but I suppose i run by you guys so I know what questions to ask. Plus its Friday night and everybody is gone
I specified that our MV SWGR be 63KAIC. The vendor does not offer 63 KAIC but offers 50 KAIC. The vendor than comes back with a method to attain 25 KAIC by the use of these Is limiters. They are to be connected at each end of the SWGR to the main circuit breakers.
1. Why would I use these Is limiters when I want 63 KAIC rather than a lower KAIC?
2. It states it is only connected to the main circuit breakers what about the feeder breakers? If the limiters are just connected to the main breakers, the feeder breakers would still be 50 kAIC?
3. Does anybody have experience with these Is limiters? Do I want to have a smaller KAIC? is it more economical?
I know these are questions to the vendor, but I suppose i run by you guys so I know what questions to ask. Plus its Friday night and everybody is gone