Hi
Im posting here because I am selling my home and am having issues with a prospective buyer who keeps referencing "code" or "nec" in regards to my garage electricity.
My detached garage has 4- 10awg wires running to it. 2 hots, neutral and ground. They are on a double pole 20A breaker. Both the 10awg ground wire and 10awg neutral wire are on the neutral bussbar inside the mainpanel. There is single pole switch at the entryway to the garage which shuts the entire garage off. There are only a few gfci outlets in the garage in addition to lighting and the gdo. There is no ground rod and these wires are buried in pvc pipe.
A prospective buyer is claiming that my setup is not up to code. That there are two circuits sharing a neutral and claims this is very dangerous since they are on a double pole breaker and not on opposite sides of the panel. He says I am likely overloading the neutral wire.
He is claiming to be "in the trades" and says in order for him to be interested I would have to bring the garage up to code by having a subpanel installed or reimbursing him to do so.
I came here because I figured this is "the" place for code issues and I wanted to gain some knowledge in order to discuss the issue with the guy.
So the bottom line, is there anything about what I describe that is against code or otherwise dangerous?
Is there any other information I can post here to clarify to you the specifics of my garage electrical?
Joan
Im posting here because I am selling my home and am having issues with a prospective buyer who keeps referencing "code" or "nec" in regards to my garage electricity.
My detached garage has 4- 10awg wires running to it. 2 hots, neutral and ground. They are on a double pole 20A breaker. Both the 10awg ground wire and 10awg neutral wire are on the neutral bussbar inside the mainpanel. There is single pole switch at the entryway to the garage which shuts the entire garage off. There are only a few gfci outlets in the garage in addition to lighting and the gdo. There is no ground rod and these wires are buried in pvc pipe.
A prospective buyer is claiming that my setup is not up to code. That there are two circuits sharing a neutral and claims this is very dangerous since they are on a double pole breaker and not on opposite sides of the panel. He says I am likely overloading the neutral wire.
He is claiming to be "in the trades" and says in order for him to be interested I would have to bring the garage up to code by having a subpanel installed or reimbursing him to do so.
I came here because I figured this is "the" place for code issues and I wanted to gain some knowledge in order to discuss the issue with the guy.
So the bottom line, is there anything about what I describe that is against code or otherwise dangerous?
Is there any other information I can post here to clarify to you the specifics of my garage electrical?
Joan