jtinge
Senior Member
- Location
- Hampton, VA
- Occupation
- Sr. Elec. Engr
Have an existing 120 v circuit to a fuel pump. Wiring is in raceways with the appropriate seals and explosion proof fittings. Fuel pump to be changed with a new pump at 208 v. Do I interpret NEC 200.7 correctly that the existing white THHN conductor cannot be reidentified as an ungrounded phase conductor so that the existing wiring can be reused at 208 v? Do the provisions allowing reidentification of the white conductor only apply to cables or flexible cords? What are my options if this is the case?