Wait...
So your nto allowed to use white THHN then recode?
And am I right in thinking that you can recode "any other color" to "any other color" as long as it's not originally gray white or green?
Kinda, except for size. If in a cable you can reidentify the white as an ungrounded 200.7(C).
If in a cord you don't have to reidentify it at all 200.7(C)(3).
You can only reidentify individual conductors larger than #6 as a gray, white, or green as Grounded or Equipment Gounding.