My interpretation would be yes. The Inspector says Schedule 80 is required. I am in Massachusetts and there is only one state code not a flavor for each town. Supply house chit chat goes both ways on this. Where is the physical damage? The depth requirements take care of that.
I have looked at:
352.10 (H) Underground Installations; shows that PVC is rated for direct burial as well as permitted to be encased in concrete See 300.5 and 305.15 (Not applicable as it is under 1000 volts. In the 2023 National Electric Code Handbook code handbook it states in the notes that “Schedule 40 and Schedule 80 are both permitted for underground installations, such as under driveways, provided that the required burial depth is met” though not official NEC it clarifies this issue.
300.5 (A) states for minimum cover requirements see table 300.5 (A)
300.5 (D) Protection from Damage
Ss (1) addresses minimum cover distance below grade to protect the conduit, no mention of Schedule 40 or 80 in this.
Ss (2) Mentions emerging from grade to 8’ needing protection I used Schedule 80 for that for the pole riser.
Ss (3) addresses the warning ribbon, which is there
Ss (4) Enclosure or Raceway Damage. More for direct buried cables that may get damaged. I assume sharp rocks, ledge or unable to meet depth requirements should use Schedule 80 or RTRC-XW (I would not consider properly installed conduit under a driveway as subject to physical damage)
Table 300.5(A) the applicable Column is 3
Location of wiring method or Circuit
“Under Streets, Highways, roads, alleys. Driveways and parking lots” The minimum cover is 24”. If you stop here you would think 24” but the location below is “One and two family dwellings driveways and outdoor parking areas, and used only for dwelling related purposes” Column 3 shows minimum depth as 18” over the Conduit and the table does not address Schedule 40 or Schedule 80 specifically.
Mass Code Amendment 300.5(A) informational note states: “Cables suitable for direct burial are often sleeved in various raceways for design reasons. If such cable is installed with sufficient cover for direct burial, then the characteristics of that raceway need not be evaluated. Other rules of this Code that apply to raceways generally may apply. See 300.5(H)”. Since the cable being installed is rated for direct burial the raceway seems irrelevant other than the fact it may want to be used differently in the future, I would want to do the job properly regardless.
Did I miss something?
Thanks in advance.
I have looked at:
352.10 (H) Underground Installations; shows that PVC is rated for direct burial as well as permitted to be encased in concrete See 300.5 and 305.15 (Not applicable as it is under 1000 volts. In the 2023 National Electric Code Handbook code handbook it states in the notes that “Schedule 40 and Schedule 80 are both permitted for underground installations, such as under driveways, provided that the required burial depth is met” though not official NEC it clarifies this issue.
300.5 (A) states for minimum cover requirements see table 300.5 (A)
300.5 (D) Protection from Damage
Ss (1) addresses minimum cover distance below grade to protect the conduit, no mention of Schedule 40 or 80 in this.
Ss (2) Mentions emerging from grade to 8’ needing protection I used Schedule 80 for that for the pole riser.
Ss (3) addresses the warning ribbon, which is there
Ss (4) Enclosure or Raceway Damage. More for direct buried cables that may get damaged. I assume sharp rocks, ledge or unable to meet depth requirements should use Schedule 80 or RTRC-XW (I would not consider properly installed conduit under a driveway as subject to physical damage)
Table 300.5(A) the applicable Column is 3
Location of wiring method or Circuit
“Under Streets, Highways, roads, alleys. Driveways and parking lots” The minimum cover is 24”. If you stop here you would think 24” but the location below is “One and two family dwellings driveways and outdoor parking areas, and used only for dwelling related purposes” Column 3 shows minimum depth as 18” over the Conduit and the table does not address Schedule 40 or Schedule 80 specifically.
Mass Code Amendment 300.5(A) informational note states: “Cables suitable for direct burial are often sleeved in various raceways for design reasons. If such cable is installed with sufficient cover for direct burial, then the characteristics of that raceway need not be evaluated. Other rules of this Code that apply to raceways generally may apply. See 300.5(H)”. Since the cable being installed is rated for direct burial the raceway seems irrelevant other than the fact it may want to be used differently in the future, I would want to do the job properly regardless.
Did I miss something?