Is splicing #6 wire with wirenuts forbidden?
pole splices
pole splices
celtic said:
How about some of these things:
Definitely prefer them...but...compare the cost vs a Big blue
If I had to do a whole bunch of parking lot poles, I would want to use the tube style crimps with a hy press tool made for the use. For speed, and for reliability, and lower cost. (Not as low as the blue nuts, but more reliable.)
Second, in situations where there is higher current such as cooktops and the like, I'll pass on the blue nuts for #6 and proceed directly to the hy-press option or split bolts.
Here's how I generally splice #6 and larger:
Materials required (MD6-8, H-Tap, H-tap cover) -
Pre-crimp setup -
Crimping process -
Crimping complete -
Do they make a bigger wirenut? Unless each pole is it's own home run, then you need to put three wires under each nut at most of the poles, and the ones posted above max out at two number six.
jbwhite said:
I didnt see that combination on the online page. It must be on the package.
I did not see it either.
Common sense tells us that a wire nut that can take one 6 AWG and two 8 AWGs could also take two 6 AWGs and one 10 or 12 AWG.
jbwhite said:
I missed the part about "if the mfg listing or labeling is not adequate use your common sense."
[:D]
"IN THE FIELD ENGINEERING"