Since the poco is requiring it and not NEC does this not make it an auxiliary” I think that is the term.
I was going to say that, but the NEC only permits Auxiliary Electrodes to be connected to Equipment Grounding Conductors. (And that more or less defines what an Auxiliary Electrode is, because there's no other definition.) So assuming there is no EGC at the meter and the utility wants the rod GEC connected to the grounded conductor, the letter of the code does not support that conclusion. I'd agree if the NEC explicitly defined Auxiliary Electrodes as electrodes not required by the NEC, but that's not the case.