I think there is an error in the handbook regarding conductor sizing and ampacity adjustment. Please review this example and let me know what you think.
We have a 25 amp continuous load. 60 degree terminals, THWN conductors, four current carrying conductors in teh raceway.
Here is the way I figure it to be done:
25*1.25 for continuous load=31.25
The conductors must have an ampacity of 31.25.
This would require an 8 AWG conductor. We then take the ampacity of 8 AWG and apply the adjustment required by 310.15(B)(2)(a), in this case, 80%. So,
40 (ampacity of at 60 degrees) * 0.80=32 amperes.
A 32 ampere conductor will carry this load, so we can use it. We would then select a 40 ampere OCPD to protect the conductor.
--------------------------------------------
Next example, same parameters:
--------------------------------------------
Determine the size of the overcurrent protective device (OCPD). Referring to 210.20(A), 125 percent of 25 amperes is 31.25 amperes. Thus, the minimum standard-size overcurrent device, according to 240.6(A), is 35 amperes.
Step 2.
Determine the minimum conductor size. The ampacity of the conductor must not be less than 125 percent of the 25-ampere continuous load, which results in 31.25 amperes. The conductor must have an allowable ampacity of not less than 31.25 amperes before any adjustment or correction factors are applied. Because there are four current-carrying conductors in the raceway, Table 310.15(B)(2)(a) applies. First calculate the ampacity of the conductor using the ampacity value calculated above:
Ampacity = computed load/0.80=39.06 amperes.
I think this is wrong
Because of the 60?C rating of the overcurrent device terminal, it is necessary to choose a conductor based on the ampacities in the 60? column of Table 310.16. The calculated load must not exceed the conductor ampacity. Therefore, an 8 AWG copper, Type TW conductor with an ampacity of 40 amperes is the minimum allowed computed load. However, conductors with a higher temperature rating such as THWN or THHN may be used, but only at their 60?C ampacity.
Which do you guys beleive to be correct...the first example, or the second?
We have a 25 amp continuous load. 60 degree terminals, THWN conductors, four current carrying conductors in teh raceway.
Here is the way I figure it to be done:
25*1.25 for continuous load=31.25
The conductors must have an ampacity of 31.25.
This would require an 8 AWG conductor. We then take the ampacity of 8 AWG and apply the adjustment required by 310.15(B)(2)(a), in this case, 80%. So,
40 (ampacity of at 60 degrees) * 0.80=32 amperes.
A 32 ampere conductor will carry this load, so we can use it. We would then select a 40 ampere OCPD to protect the conductor.
--------------------------------------------
Next example, same parameters:
--------------------------------------------
Determine the size of the overcurrent protective device (OCPD). Referring to 210.20(A), 125 percent of 25 amperes is 31.25 amperes. Thus, the minimum standard-size overcurrent device, according to 240.6(A), is 35 amperes.
Step 2.
Determine the minimum conductor size. The ampacity of the conductor must not be less than 125 percent of the 25-ampere continuous load, which results in 31.25 amperes. The conductor must have an allowable ampacity of not less than 31.25 amperes before any adjustment or correction factors are applied. Because there are four current-carrying conductors in the raceway, Table 310.15(B)(2)(a) applies. First calculate the ampacity of the conductor using the ampacity value calculated above:
Ampacity = computed load/0.80=39.06 amperes.
I think this is wrong
Because of the 60?C rating of the overcurrent device terminal, it is necessary to choose a conductor based on the ampacities in the 60? column of Table 310.16. The calculated load must not exceed the conductor ampacity. Therefore, an 8 AWG copper, Type TW conductor with an ampacity of 40 amperes is the minimum allowed computed load. However, conductors with a higher temperature rating such as THWN or THHN may be used, but only at their 60?C ampacity.
Which do you guys beleive to be correct...the first example, or the second?