PG&E requires unfused disconnects? All my projects use fused disconnects because the unfused disconnects only have a 10kAIC rating and most of the time on a supply side interconnection in a C&I project the fault current is more than 10KA.
Here is a link to the PG&E spec for disconnect switches: http://www.pge.com/includes/docs/pd...lity/electrictransmission/handbook/060559.pdf
It states that you cannot switch the neutral (item 7).
One of the functional requirements is:
- A fusible ac disconnect switch is required for generators that do not have over-current protection (i.e., breakers, fuses) at the point of interconnection with the utility.
So if the generator does not have OCP you have to use a fused disconnect, for others it is an option.
An Eaton DG222URB or equal with the optional neutral kit would probably work for you if you don't need a higher AIC rating.
Well, unfused disconnects don't really have a KAIC rating, because they cannot automatically do the function which starts with the letter I in that initialism. They have an SCCR rating instead, which is usually 10 kA.
It is very counterintuitive that an unfused disconnect would have such a weak SCCR rating, because they are usually built with exactly the same main components as their fused counterparts, which have a 200kA SCCR rating.