Is there a better way??

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
So each floor we have two electrical closets and (6) tenant spaces. Each tenant space is feed from a tenant distribution board in main closet to trough/equipment as you see below. For the grounding( see below) they are asking us to run 1-1/2" and 4/0(note not shown below) from ground bar in electrical closet to each tenant space. Not even sure where we would land in the tenants space( only shows the line/arrow below). Maybe at the transformer or another ground bar?

1. Do you thin this is require from ground bar to each tenant space( the 1-1/4 & 4/0?
2. Is do where could the ground land at the tenant space? Somewhere at the distribution equipment or xfrmr or a ground bar?
3. Anyway this run might not be needed? Thanks


View attachment 2581677



View attachment 2581678
 
Are there transformers being installed? What it the construction type of the building, is there building steel? A poured concrete building would require some sort of common grounding riser if there are transformers involved.
 
Are there transformers being installed? What it the construction type of the building, is there building steel? A poured concrete building would require some sort of common grounding riser if there are transformers involved.
No building steel. As picture shows there is grounding risers
 