electrofelon
Senior Member
- Location
 - Cherry Valley NY, Seattle, WA
 
- Occupation
 - Electrician
 
Came across a few situations recently that got me thinking.  Situation #1: Installed a service disconnect that had three switches as the main.  The service conductors were 205 amp ampacity and it was a 400 amp MLO I-line panel.  Inspector said I needed a plaque stating that the ampacity of the conductors was 205 amps.  This is a state code (WAC) here in Washington that I did know about but it slipped my mind.  i understand the theory that someone could see the 400 rated panel and connect a feeder or branch circuit that is more than 205 amps.  Situation#2:  House that is fed from a meter/main on a pedestal several hundred feet away.  The house is fed with a 125 amp feeder not service conductors.  The HO was picking up the panel and I told him to just grab a 200 main breaker panel because it only needs a disconnecting means not overcurrent protection and the 200 amp panel has more spaces and is basically the same price as a 125.  Situation#3:  You have some 15 amp rated circuits that for any number of reasons are 12 gauge going into the panel.  When this happens I label them "15amp only".  Is there anything in the NEC that would require labeling that the capacity/rating is not what it appears in these or similar situations?
	
		
			
		
		
	
				
			
				